Can you also reproduce this in a completely new activity and macro sequence? Integrations have not influence on sequences. And according to the log all commands are executed.
Do you have any other device to test with the integration to rule out any problem with the light manager?
And can you combine the integration and request logs and reduce the lines to a minimum? Maybe there are core request that don’t reach the integration.
I still think this is a remote side problem as the sequence position seems to change the behavior and there are no integration errors. Can you confirm that you have 2.11.0 installed?
I don’t know how to apologize to you for the inconvenience.
The problem ultimately lays with the LM scene. With a different scene, everything works as expected.
The difference is that the scene numbers were NOT BOTH two-digit numbers. One was two-digit, the second was one-digit. Now, with two-digit scene numbers for both scenes, everything works perfectly.
I don’t know how that can lead to the problem, but apparently it is the cause of the problem.
What I don’t understand is: when I send the two commands with the different numbers via HTTP GET, they work.
You can use “send command” instead. This offers a delay parameter. But keep in mind thats using send command currently doesn’t change the power attribute.